Maximum span of flat roof joists
With access for maintenance and repair only or unlimited access?
Imposed load 0.75 kN/m2, 1.0kN/m2 or 1.5kN/m2?
Strength Class C16 or Class C24?
Dead loads (kN/m2) excluding self-weight of joist of less than 0.5, 1.0 or 1.5?
Spacing of joists 400, 450 or 600mm?
nearest available size will be 47 X 220mm.
Thanks for your reply
400 centres the span is 5200 I was hoping to get away with using joists rather than dropping in a steel to split the span
What size joists would I need for that span and at what centres
ok just been looking at the strada tables for flat roof joists
its saying the maximum span for a 47 x 220 joist at 400mm centres for maintenance and repair only is 5.34 m
as my clear span of joist is 5150mm according to this table a 47 x 220 is sufficient
does anyone else go by these tables and are they reliable?