MCB unit

boughtonpat, you will see from the various posts that most likely you will not be able to safely install the 10KWatt shower.

The electrician gave you poor advice since even a 40amp MCB would not be appropriate for a 10Kwatt load. The electrician should have provided you with much more advice. It is also quite likely that the existing cable is not appropriate for a 10KWatt load. Any attempt to install the shower without ensuring the cable is appropriate will likely lead to a fire.

You have two choices

1) Take the shower back and buy 7KW/7.5KW shower.
2) Contact a registered electrician and have them quote you for the work required to install a 10KW shower.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.