Selection and errection! i all depends on the environment it is placed, T+E will be suitable in some environments SWA in others SWA with a 6mm steel capping will be required in others, MICC is only suitable if there is no vibration perfect cable routes etc, i've inspected countless installations of MI which have failed due to poor termination or installation, why people still use it for other than essential fire proof circuits is beyond me.
Aesthetics
Reduced cable size
Less risk if overloaded
If installed correctly it will last indefinatly
Fire & explosion proof
Has its own mechanical protection
BTW it can be used where vibration is present.
For example if a motor is fed in pyro, there is no problem providing a loop has been put between the last fixing and the motor.
We fit loads of pyro on non fireproof installations, especially old churces and the like. Done right, you will not get a neater, more discreet installation.
we should look at europe they use rigid round cable a million times better for the majority of installations than MI SWA T+E etc sorry but MI is so last century it costs a futune to install i can see your the resons for your arguements but those are special installations, if the installation is designed correctly the risk of overload should not exist! explosion proof!! i find SWA is stronger at the terminations which is where MI fails! causing explosion and fire..........
There is nothing on the market that is fire proof except MICC. So last century? This isnt Gucci we're talking about here. Its the best practical solution for a fire alarm per se. It is still specified so it is still modern. In my experience, those who dislike it have problems when installing it.
i'll happly install it if it is necessary, but very rarely do, having said that i dont install alot of cable these days. " There is nothing on the market that is fire proof except MICC" as i said special installations. i see so many badly installed cables of all types. on a inspection of a filling station i carried out recently there was a newly installed LPG pump very well installed MICC cables with vibration loops etc explosive proof starter etc on closer inspection there was a un blanked cable entry in the motor TB!!
Aesthetics....We fit loads of pyro on non fireproof installations, especially old churces and the like. Done right, you will not get a neater, more discreet installation.