Darren, firstly lose the caps lock, that is considered shouting.
To answer your question we need some information;
Why is the distance from meter to board 7 meters?
Is this existing or have you moved it?
If existing what cable fed the board before?
What size mains supply do you have (60A, 80A, 100A, 125A)
Generally the link from meter to board should not exceed 2 meters if using double insulated tails. If the run is greater than this, then a different type of cable should be used, generally this will need to be SWA (Steel Wire Armoured) as the largets Twin and Earth (T&E) cable available is 16mm. The usual head is 100A, thus you need to have a 25mm cable, but depending on the load your installation runs at, you may need to consider 35mm (although this is unlikely).
The SWA will not terminate straight into your meter, so it would need to be terminated in a steel box to ensure it is terminated correctly, ideally your DB will be steel too. Either way the integrity of the Earth must be maintained from supply to DB, this can be done with the armouring of the SWA, but you may wish to consider the purchase of 3 core SWA so that the third core is your Earth. All connections must be tight, as tight as possible without damaging the screw heads.