Mira Shower Tripping Out - Cabling Melted (With Pics)

....but that's the first time I've seen the CPC's on harmonized T&E....

Could you explain what you mean, I don't get the terminology :oops: :P

No problem.
CPC = 'The earth cable' - Circuit Protective Conductor
Harmonized = Our use of Blue/Brown/Green & Yellow cabling instead of Red/Black/Green to pacify our European friends.
T&E = Twin (brown & blue) & Earth (green & yellow)

:)
 
Is it just verdigris on the CPC or has a substantial fault current flowed at some stage?
 
I got round to sorting this mess out tonight.

Bought a new pole switch as the old one only had one earth terminal, hence why I think it was badly twisted together. Trimmed the butchered cabling up and put some sleeving on the earths :wink:

img3238640x480.jpg


Got the 60amp choc blocs (as recommended) and it's a perfect fit to where the original terminal block was fitted.
Sleeved the earth again and I also left about a 0.5m run in the loft, just incase this ever happens again - I won't have to re-run the cable in the wall, just snip the end  8)

img3237640x480.jpg


All is working fine now, so fingers crossed it stays that way!
Thanks alot for all the help. Very much appreciated

Lee
 