Finally in the process of laying under floor heating. I have fitted a RCD FCU, on the supply, do I also need some other means of isolation for the circuit.
If so, I guess it will go between RCD and Stat ?? Is that correct ?
Thanks again.
What load design have you calculated for the UFH ?
How will you use it ? Constant on, stat set, stat and timer, manual ?
It would be prudent to have some sort of on/ off control and I can't suggest anything because I have no idea of the load, a switched f/spur or a DP 20a switch at a guess.
If an FCU is man enough to supply the load then it can be used as local isolation.
Sorry guys.
It is a 700W cable. (70m@10W per M).
So by my calculations, drawing 2.9A
It will be used mainly on a timer and I was only planning on using the stat as an isolation point to be honest, until a friend said it should be further isolated !!! He is not a spark though ! So thought I'd ask someone in the know on here !
calc should be done with voltage at 230v not 240v so it's a tad over 3 amps.
Switched fuse spur and 5a fuse would be best. What rated fuse did you use at the CU ?
thanks Chris,
Yeh, wasn't too sure wether to use 230v or just the nominal, but thanks.
I was going to use a 5A fuse, so you have confirmed that what I was doing originally was fine.
Thanks again to all replies. The saga continues !!!!!!!!