Back again for more advice & opinions on electrical matters! Hope I get my terminology correct in what follows....
After recently sorting out the outside socket thanks to previous help on here, I'd become aware of 2 x T&E cables leaving a 32A MCB in the CU dedicated to the garage circuit. Initial thoughts were it was a ring... but one of the cables appears to be 4mm and the other a 2.5mm. Therefore, I was curious regarding the design of the garage circuit.
Bit of background info. The previous owner had partly converted the garage - fully plasterboarded, carpeted, cupboards and utility area / boiler. This obviously makes it trickier to trace cables etc.
Working safely (after isolation, checking for dead etc) I concluded that the 2.5mm cable ran only to a double socket on the nearest wall (no spurs off this socket). The 4mm cable ran to a double socket the other side of the garage, a spur off this to another double socket (in 2.5mm), and off this socket ran 2 x spurs (in 2.5mm) to 2 x FCU's - one for the boiler, one for the outside socket.
Not great, but at least I could see what had been done. [Is a 'Radial' the correct term for that configuration ??]
However... another double socket appeared to be fed from the 4mm cable as with everything but the 4mm connected, its live. As its not spurred from any socket, my conclusion is there must be a hidden junction box somewhere along the path of the 4mm cable, but just where I can't tell and if I start ripping up the walls & ceiling the wife will not be happy!
Anyway, for now I've swapped the 32A MCB for a 20A (more than adequate for current demand) which I'm hoping at least makes the situation somewhat 'safer' ? - was that a reasonable move?
Thanks in advance....
(I have another question but one thing at a time eh!)
After recently sorting out the outside socket thanks to previous help on here, I'd become aware of 2 x T&E cables leaving a 32A MCB in the CU dedicated to the garage circuit. Initial thoughts were it was a ring... but one of the cables appears to be 4mm and the other a 2.5mm. Therefore, I was curious regarding the design of the garage circuit.
Bit of background info. The previous owner had partly converted the garage - fully plasterboarded, carpeted, cupboards and utility area / boiler. This obviously makes it trickier to trace cables etc.
Working safely (after isolation, checking for dead etc) I concluded that the 2.5mm cable ran only to a double socket on the nearest wall (no spurs off this socket). The 4mm cable ran to a double socket the other side of the garage, a spur off this to another double socket (in 2.5mm), and off this socket ran 2 x spurs (in 2.5mm) to 2 x FCU's - one for the boiler, one for the outside socket.
Not great, but at least I could see what had been done. [Is a 'Radial' the correct term for that configuration ??]
However... another double socket appeared to be fed from the 4mm cable as with everything but the 4mm connected, its live. As its not spurred from any socket, my conclusion is there must be a hidden junction box somewhere along the path of the 4mm cable, but just where I can't tell and if I start ripping up the walls & ceiling the wife will not be happy!
Anyway, for now I've swapped the 32A MCB for a 20A (more than adequate for current demand) which I'm hoping at least makes the situation somewhat 'safer' ? - was that a reasonable move?
Thanks in advance....
(I have another question but one thing at a time eh!)