Discussion in 'Plumbing and Central Heating' started by TheSirSpence, 4 Apr 2019.

  1. TheSirSpence

    TheSirSpence

    Joined:
    4 Apr 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    SOLUTION:

    The solution is the following:

    [​IMG]

    Could not have come up with it without the help of @ianmcd


    Hi all,

    I have had my boiler switched out from an very old (1990s) boiler to a Glow Worm 30c.

    I had a Nest configured on this by an official installer, I believe he used the Y Plan configuration.

    The new boiler is installed but the Nest is not connected in any way. I believe it should be easy enough to do, but I need a little guidance.

    Here are what I believe are the relevant diagrams:

    NEST

    [​IMG]

    BOILER

    [​IMG]

    Is that really all there is to it, two wires between the boiler and heatlink? How do I turn off the timer on the boiler? do I need to remove either of the loops under X106 on the second diagram?

    One of the confusing things I am seeing in my research is this diagram:

    [​IMG]

    I know its for a slightly different boiler the 30CX rather than 30C, but that seems to indicate 4 wires..... which is fine, but I do not see a 0v socket on the boiler.

    Would someone mind pointing me in the right direction please?
     
    Last edited: 8 Apr 2019
  2. Sponsored Links
  3. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,499
    Thanks Received:
    8,376
    Location:
    Lanarkshire
    Country:
    United Kingdom
    2&3 from the nest are connected to your boiler at plug X106, you will see the terminals marked 24vRT you remove the link (if still fitted) and connect the two nest wires to here, do not put 240v into those terminals
     
    • Thanks Thanks x 1
  4. TheSirSpence

    TheSirSpence

    Joined:
    4 Apr 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks Ian, If I am reading it right, does this mean it will look like this:

    [​IMG]

    Also it doesn't seem clear which way round 2 and 3 connect to in X106
     
    Last edited: 5 Apr 2019
    • Like Like x 1
  5. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,499
    Thanks Received:
    8,376
    Location:
    Lanarkshire
    Country:
    United Kingdom
    yep that is correct, doesnt matter which way round in X106 its just a switch
     
    • Thanks Thanks x 1
    • Like Like x 1
  6. TheSirSpence

    TheSirSpence

    Joined:
    4 Apr 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    THANKS IAN!! I think it is all wired up and connected correctly, do I need to set the boiler to any particular setting to get the heating to come on or off? at the moment it is set to the timer but ideally I would want that off entirely.

    UPDATE: It is working, I have it set to on and the Nest seems to take control.
     
    Last edited: 4 Apr 2019
  7. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,499
    Thanks Received:
    8,376
    Location:
    Lanarkshire
    Country:
    United Kingdom
    just set the timer to constantly on, and the nest will control everything
     
    • Thanks Thanks x 1
  8. TheSirSpence

    TheSirSpence

    Joined:
    4 Apr 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Awesome thanks so much Ian
     
    • Like Like x 1
  9. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  10. Sponsored Links
Loading...

Share This Page