New consumer units help!!!!
13 Mar 2007
Wiltshire
HI guys need a bit of advice from any sparkies out there!
Question: I have 2 old fuse boards side by side,1 is economy 7 i believe.
I had a spark look at it and quoted £500 to replace,which is better than the £2000 the s.e.board quoted!!
Now is it ok 2 replace the 2 fuseboards with 1 new large c.unit using a split board? as this is what the sparky said he would do,or do i need to still have 2 fuse boards?The idea seemed ok to me as he explained it but i just wanted to ask you guys to make sure!!
Any advice much appreciated!
depends on what sort of Economy seven you have, some have two sets of separate meter tails one for on and one off peak supplies, and others use a dual tariff meter with one set of tails and a teleswitch to change it over. he could install a board with two main switches in it and an RCD so you would effectiveley have a split load board and an off peak board in the same enclosure. His price sounds a bit low to me, is this including a full test and report on the house wiring ,as if carrying out a board change this should also be done and a certificate issued for it.
Nick
Thanks for you reply nick,to me it looks like there are 2 main feeds one to each existing fuse board,he said the new C.Unit will have 2 independant mains switches so basically making 2 boards out of one unit is what he said.Im not sure of the certificate i shall clarify this with him,he seems to be genuine but i shall confirm,is there a specific name for this particular certificate?
probably a double-decker CU
it won't hurt to see what brand he is budgeting for.
It's not Chinese, is it?
Prob 2 x proteus CU's double decked with the jointing adaptors.
I have only used a Proteus CU once - NEVER again
Ok guys apparently he is going to use the following Consumer unit to replace the 2 existing old fuseboards!
MK Split Consumer Unit. 16 module. 12-Way. Pre-assembled. Supplied with switch, 100A DP Isolator, 80A 30mA RCD, 2 cover mounted blanks and 10 MCBs. Insulated with floating busbar. 10 year manufacturer's guarantee.
He tells me the main switch will feed the economy 7 circuits and the RCD main switch will feed the rest of the circuits independantly and this will meet the safety requirements!
Does this sound ok?
MK board - OK, although would use double decker CU.
One din rail for e7 circuits fed off isolator - OK.
Other din rail for all other circuits fed off RCD - many sparks on here including myself think it is very bad practice to run the lighting and sockets etc off the same RCD, I think that your spark should configure the rest of house din rail to be split load.
BUT that would depend on the earthing arrangements for the house, do you have a suppliers earth or do you have an earth rod??
Ought to have one overall Isolator for the installation as well
I'd probably get a normal split board for the normal stuff, and a Isolator board for the E7 put them side by side, clearly labeled, and have a 4 pole isolator nearby to switch both sets of tails
perhaps he is suggesting the MK split-load as it is readily available at good discounts and he uses it a lot. It is a good brand though no longer one of the best. The suggested layout would work but is not ideal.
a dual-tariff double-decker would be more suitable and a little more expensive (probably not stocked by the discounters). So would a 2-board layout.
Compared to the total cost of installation including testing, rectification and certification, the extra cost of a better unit would not be very significant.
I agree it is poor practice to have a number of circuits controlled by a single RCD (especially if it includes lighting, cooking and water-heating).
If there are only the typical two socket circuits needing RCD protection it might be worth using RCBOs rather than a split load (especially if the alternative is not heavily discounted).
I like Adam's 4-pole isolator, not very expensive but I suspect not often seen in domestic installs.
I think so, but you can remind me if you like. :wink:
Personally not that keen on them as you cannot tell the difference between overload and earth faults!
a fair point, but leakage trips are more common round here.