I have just bought a new electric oven and was wondering if the connection i have is ok to connect it to.
I have a 45amp double pole switch with 6mm cable running off for about 3 meters to the consumer unit this is fused with a re-wireable 30amp.
There is also some 6mm cable running from the switch that will if ok connect to the cooker, this runs about 1.5meter.
The cooker is an indesit a link to check out electrical spec is below.
http://imagebank.indesitcompany.co....t/Cooking/K3E1G_K3E11G_K3E1IR_19504968202.pdf
Hope someone can help with this one thanks.
I have a 45amp double pole switch with 6mm cable running off for about 3 meters to the consumer unit this is fused with a re-wireable 30amp.
There is also some 6mm cable running from the switch that will if ok connect to the cooker, this runs about 1.5meter.
The cooker is an indesit a link to check out electrical spec is below.
http://imagebank.indesitcompany.co....t/Cooking/K3E1G_K3E11G_K3E1IR_19504968202.pdf
Hope someone can help with this one thanks.