Just tried opening the TRV again and nothing but a slow drip. The pipe is also still cold. Maybe this could be an indicator that the valve is not fully opening?
Also, maybe the water on the lockshield side became hot because this is residual heat in the return pipe that made it's way back and out of the lockshield valve when it was opened?
Also tried opening the TRV while the lockshield was open but didn't make any difference, water still drips slowly out of the TRV.
I then played around with the TRV pin to try to "release" it i.e. pushed it closed and open a few times. The drip did indeed appear to increase and I felt some mild warmth appear in the pipe.
This suggests to me the issue is the TRV valve so I will go ahead and replace this after lunch and fingers crossed that will resolve the issue.
I can confirm the boiler pressure is still okay, at 1.4 bar while the boiler and pump are on.