No heat ! Grant boiler low pressure - will not fire

Joined
1 Jul 2012
Messages
40
Reaction score
0
Location
England
Country
United Kingdom
I have a Grant Vortex Oil boiler that will not fire, so we have no heating or hot water at the moment.

The Low Pressure light comes on, so I have turned both black taps on but nothing happens (I was expecting the sound of rushing water). This is what I have done so far:

I disconnected the fill loop hose at both ends and checked that it isn't blocked.

I reconnected the bottom of the hose and opening the bottom tap sends water through the hose ok.

I have checked that the black taps actually turn the brass knob beneath them.

I have checked the stop cock and it's on full and water pressure seems ok.

The gauge is reading 0.25 at the moment and doesn't move when the taps are open. The house has been empty for a few weeks so we don't know when it stopped working.

Can anyone suggest anything else to try?
 
This is connected
IMG_20260225_133128507_HDR.jpg
and this is top disconnected and top tap open
IMG_20260225_190213932_HDR.jpg
 
The top valve is a check valve ( one way flow only), and it's jammed / stuck closed .
 
Thanks. If I turn the water off at the stopcock, can I just remove this valve and pick a new one up at a plumbers merchant?
 
Is that an arrow on the side pointing down? If so it's the wrong way round.
Actually I think it should be pointing down anyway. There is a separate isolation valve on the cold inlet, on top of the boiler, is that open and working?
 