Oil Boiler Goes Bang!

Discussion in 'Plumbing and Central Heating' started by leakydave, 5 Sep 2011.

  1. leakydave

    leakydave

    Joined:
    2 Nov 2005
    Messages:
    959
    Thanks Received:
    102
    Location:
    Gloucestershire
    Country:
    United Kingdom
    [code:1]

    A customer rang me on Saturday evening: his Thermecon System 100/150 oil boiler had gone BANG, blown the casing off and the combustion chamber cover plate had been blown upwards/outwards and now has a nice curve to it. [see photo]

    The boiler continued to fire and fill his utility room with combustion fumes.

    I rang the manufacturer today, and was advised that it was probably caused by ' a period of low voltage'.

    My customer is concerned because he reckons his house could have burnt down if he happened to be out.

    What would you advise: new boiler [old one 10 yrs old] or replace the chamber cover and keep the fire brigade on stand by?[/code:1]
     
  2. Sponsored Links
  3. Youllneverguess

    Youllneverguess

    Joined:
    5 Sep 2011
    Messages:
    389
    Thanks Received:
    39
    Location:
    Bedfordshire
    Country:
    United Kingdom
    New boiler.
     
  4. DeltaT2

    DeltaT2

    Joined:
    24 Aug 2011
    Messages:
    1,400
    Thanks Received:
    165
    Location:
    Glasgow
    Country:
    United Kingdom
    Low voltage is complete ball.x!! Fuel in the combustion chamber after it shuts off. Then it re-fired & BANG!! Seen it before on post purge type burners with jammed silinodes. Don't you just love boiler manufactures lying sh.ts!!
     
    • Thanks Thanks x 1
  5. xr4x4

    xr4x4

    Joined:
    1 Oct 2009
    Messages:
    3,159
    Thanks Received:
    290
    Location:
    Hampshire
    Country:
    United Kingdom
    Crikey.....that's taking 'delayed ignition' to the extreme...!
     
  6. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,139
    Thanks Received:
    510
    Location:
    Shropshire
    Country:
    United Kingdom
    My customer is concerned because he reckons his house could have burnt down if he happened to be out.

    What would you advise: new boiler [old one 10 yrs old] or replace the chamber cover and keep the fire brigade on stand by?[/code][/quote]

    First, assess what other damage has been done, to baffles etc. Then replace the solenoid valve, or fuel pump depending on the pump.
    If the installation has a fire valve correctly positioned and operating, that should stop his house burning down.
     
  7. ChrisOxford

    ChrisOxford

    Joined:
    25 Nov 2007
    Messages:
    491
    Thanks Received:
    60
    Location:
    Oxford
    Country:
    United Kingdom
    Can this scenario happen with current models too? Might help the OP decide whether to replace or repair.
     
  8. DeltaT2

    DeltaT2

    Joined:
    24 Aug 2011
    Messages:
    1,400
    Thanks Received:
    165
    Location:
    Glasgow
    Country:
    United Kingdom
    I'd advise a new HE boiler, for starters I'd not trust the burner on the old boiler!
     
  9. Youllneverguess

    Youllneverguess

    Joined:
    5 Sep 2011
    Messages:
    389
    Thanks Received:
    39
    Location:
    Bedfordshire
    Country:
    United Kingdom
    A fire valve won't put out a fire or call the fire brigade. It will only stop more oil feeding in.

    Replace the boiler.
     
  10. Sponsored Links
  11. Boilerman2

    Boilerman2

    Joined:
    10 Jun 2009
    Messages:
    5,225
    Thanks Received:
    1,015
    Location:
    Suffolk
    Country:
    United Kingdom
    As parts are still availible I'd fix the existing boiler I suspect the delayed ignition could be due to arcing of the ignition electrode block on the Ecoflam Minor Burner especially if they are the monoblock Brown colured variety, replace the electrode block check the solenoid valve is holding shut - but i would gamble that the ignition electrode was the root cause of your minor explosion! ;)
     
  12. leakydave

    leakydave

    Joined:
    2 Nov 2005
    Messages:
    959
    Thanks Received:
    102
    Location:
    Gloucestershire
    Country:
    United Kingdom
    The fumes were shooting out of the top of the boiler... the fire valve is positioned above the burner.
     
  13. Gasop

    Gasop

    Joined:
    25 Oct 2009
    Messages:
    313
    Thanks Received:
    44
    Location:
    Southampton
    Country:
    United Kingdom
    Have damaged components and burner replaced and set up by competant oil boiler
    operative.

    This is a very rare occorence for an oil boiler ( never heard of this before)

    No need for new boiler (10 years is no age for oil boiler)

    Much, much cheaper than new boiler ;)
     
  14. DeltaT2

    DeltaT2

    Joined:
    24 Aug 2011
    Messages:
    1,400
    Thanks Received:
    165
    Location:
    Glasgow
    Country:
    United Kingdom
    Have damaged components and burner replaced.................

    Good luck with that!!! Gawd knows what all has been damaged inside the combustion chamber and how well you can seal all items that have been twisted & damaged!! And how long the water jacket will hold up??
    Just replace the boiler & your customer will sleep at night.
     
  15. ChrisOxford

    ChrisOxford

    Joined:
    25 Nov 2007
    Messages:
    491
    Thanks Received:
    60
    Location:
    Oxford
    Country:
    United Kingdom
    That's a good point. Even if you can repair it, there will always be that nagging doubt in the back of the customer's mind.
     
  16. dcawkwell

    dcawkwell

    Joined:
    2 Nov 2010
    Messages:
    3,422
    Thanks Received:
    516
    Location:
    Humberside
    Country:
    United Kingdom
    New boiler this one is scrap.

    Low voltage indeed.
     
  17. ChrisOxford

    ChrisOxford

    Joined:
    25 Nov 2007
    Messages:
    491
    Thanks Received:
    60
    Location:
    Oxford
    Country:
    United Kingdom
    And if that is the true reason, periods of low mains voltage ("brownouts") are so common that this kind of thing must happen all the time! Surely cause for a safety recall?
     