The sludge might have been depositied elsewhere as well but w'll see.Yes I did look into F&E cistern and it is fine - no sludge build up (I drained the system down in June and cleared all the sludge that was there and there was a fair bit of that).
Yes I did look into F&E cistern and it is fine - no sludge build up (I drained the system down in June and cleared all the sludge that was there and there was a fair bit of that).
I am not sure how long it takes to reheat the cylinder as I did not have to use HW for a while after it went cold last time.
I will take the flow/return readings next time I am up there.
With venting air from it am I risking anything (obviously with the boiler etc turned off)? I just do not want to create any more problems for myself![]()
Don't bother with that venting, the AAV will get rid of it eventually or the thumbvent until its installed.
The flow/return readings should tell something.
Did you notice if the valve that you checked full open was in the coil return only and wasn't a by pass betwwen the coil flow & return, can be checked the next time anyhow.