Oven & Hob wiring

Joined
29 Jan 2005
Messages
6
Reaction score
0
Country
United Kingdom
Am replacing existing oven & hob with Oven rated at 4.2kW and Hob rated at 6.6kW. Consumer unit is approx 20m from cooker unit. I think I need 10mm cable supply to cooker unit (and 45amp MCB), but would a 6mm cable suffice?
Grateful for some advise.
Thanks
 
Sponsored Links
jesus man, don't just guess. have you brought other factors into consideration?

Instalation Method?

is there a 13a socket on the cooker control unit?
 
Not just taking a guess! No 13amp socket with cooker unit. Current cooker unit on direct supply from CU via a 20A MCB (and 2.5mm cable). Understand I will have to change the supply cable size, just need to know whether to use 6mm or 10mm.
 
id put the new oven on the existing 2.5mm with a 20A breaker and run 6mm for the new hob with a 32A breaker.
 
Sponsored Links
Would prefer to keep it at one cable and one MCB rather than the 2 you suggest.
 
albarker said:
Would prefer to keep it at one cable and one MCB rather than the 2 you suggest.
any reason why? is there no fre spaces? i would do as plug mentioned and have the on seperate MCB's. means that if there is a fault, only 1 will go off
 