Oven needs wiring to a dedicated circuit?

Discussion in 'Electrics UK' started by jacoscar, 17 Nov 2021.

  1. jacoscar

    jacoscar

    Joined:
    30 Aug 2019
    Messages:
    240
    Thanks Received:
    2
    Country:
    United Kingdom
    Jus looking at a new electric oven and the specs say:

    INSTALLATION
    Electrical installation This product requires hardwiring to a 16 Amp fuse and should be installed by a qualified installer, such as one of our Team Knowhow experts.
    Power supply 16 Amp (Requires hardwiring to a dedicated circuit)

    What does this mean? Does it need a dedicated 16A circuit from the CU or is a 16A fused spur from the ring enough?


    I think a spur should be able to carry 26A as that’s 2x13A plugs

    Are they just trying to confuse me so I pay their KnowHow installation?
     
  2. Sponsored Links
  3. RandomGrinch

    RandomGrinch

    Joined:
    15 Jun 2021
    Messages:
    1,568
    Thanks Received:
    342
    Location:
    Wales
    Country:
    United Kingdom
    Hi,

    Sometimes appliance instructions are just wrong!
    However, in this case we will need the make and model to confirm.

    If this is a single oven and it is rated at 16A, then no, it is not advisable to connect it to an FCU. Only 13A FCU's are available, and you may constantly be blowing fuses (Edit: well probably not, given the sustained current capacity of a 13A fuse - still not a good idea though!).

    You will need a dedicated cooker circuit, and if you were to get one installed, get at least a 32A circuit (for future proofing)!

    If you haven't bought the oven yet, and you only have a plug socket available, then look for a 'plug in oven':
    https://ao.com/l/electric_single_ovens-14596/1-20/42-43-45/
    They will be rated at under 3kW and may even come fitted with a plug!

    If you want some more opinions, you may wish to get this post moved to the 'Electrics UK' forum :)
     
    Last edited: 17 Nov 2021
  4. jacoscar

    jacoscar

    Joined:
    30 Aug 2019
    Messages:
    240
    Thanks Received:
    2
    Country:
    United Kingdom
    Thanks,
    this is the oven I was looking at

    https://www.currys.co.uk/gbuk/house...JNkNb0Guj1xWX46a-1BoCJ0AQAvD_BwE&gclsrc=aw.ds

    I noticed some only mention ‘a 16A fused connection’, but if as you say, they don’t exist/are illegal, it automatically becomes a new circuit from the CU

    Unless there is another way I don’t know


    how do I summon a moderator?

    Moderators, if you’re listening, could you move this to ‘electrics UK’, please?
     
    Last edited: 17 Nov 2021
  5. RandomGrinch

    RandomGrinch

    Joined:
    15 Jun 2021
    Messages:
    1,568
    Thanks Received:
    342
    Location:
    Wales
    Country:
    United Kingdom
    If you click 'report' under your message, and just give the reason - simple :)
     
  6. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,327
    Thanks Received:
    571
    Location:
    London
    Country:
    United Kingdom
    Once again, yet another example of manufacturers instructions being wrong.
     
  7. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,854
    Thanks Received:
    451
    Location:
    Kent
    Country:
    United Kingdom
    How is it wrong?
     
  8. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,327
    Thanks Received:
    571
    Location:
    London
    Country:
    United Kingdom
    They are asking to use something which does not exist.
     
  9. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    26,039
    Thanks Received:
    2,595
    Location:
    Bedfordshire
    Country:
    United Kingdom
  10. Sponsored Links
  11. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    10,099
    Thanks Received:
    2,037
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Perhaps.
    What circuit(s) have you already got for oven/hob/cooker ?
     
  12. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,327
    Thanks Received:
    571
    Location:
    London
    Country:
    United Kingdom
  13. jacoscar

    jacoscar

    Joined:
    30 Aug 2019
    Messages:
    240
    Thanks Received:
    2
    Country:
    United Kingdom
    I currently only have a gas oven, there is a single socket outlet behind it for the gas hob igniter, which I suspect is a spur (unfused) of the ring
     
    Last edited: 17 Nov 2021
  14. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,854
    Thanks Received:
    451
    Location:
    Kent
    Country:
    United Kingdom
    OP has quoted ‘a 16A fused connection’, this is not the same thing a 16A FCU.
    OP has even made the distinction between the two
    ‘a 16A fused connection’ and (Requires hardwiring to a dedicated circuit) is easily complied with by a 16A fused radial.
     
  15. RandomGrinch

    RandomGrinch

    Joined:
    15 Jun 2021
    Messages:
    1,568
    Thanks Received:
    342
    Location:
    Wales
    Country:
    United Kingdom
    It's a single oven so no chance of diversity calculations.
    But at 3200W, that is so close to 13A!

    Edit: 3.2kW@240V from the manual. 2.94kW by my calcs at 230V ;)

    Although to be clear, i would definitely not connect it to a plug or FCU!
     
    Last edited: 17 Nov 2021
  16. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,854
    Thanks Received:
    451
    Location:
    Kent
    Country:
    United Kingdom
    even closer to 14A and we all know how hot these units run at full power. I'd do my best to avoid the overloaded situation.
     
    • Like Like x 1
  17. jacoscar

    jacoscar

    Joined:
    30 Aug 2019
    Messages:
    240
    Thanks Received:
    2
    Country:
    United Kingdom
    If I run a new radial circuit do I also need a switch in the kitchen to turn the oven off (whether over the countertop or inside a base unit next to the oven) or would the MCB suffice for the sake of isolating the oven without having to physically touch it?
     