Oven power requirements

Or on the back by the power connections.

If you look in the installation manual it says "check the rating plate".

Try calling Bosch helpdesk iIf you cant find it.
 
It will need its own radial.

4.4KW is just under 20A, so you should be ok with a 20A breaker. I'd use nice thick supply cable for future proofing. 6mm should do it.
 
Surely its always a good idea to overspec things like that when it no doubt involves digging up the floor etc?

The cost of the larger cable is insignificant when taken in context of the whole job.

Also depends where the cable is routed as to wether 2.5 would be fine.
 
Electrician fitted a 20A radial for it using 6mm cable this morning. Kitchen's bare and ceiling was down so fairly easy from what I saw.
 