Hi Guys
Today, I are mostly a punter: I can't figure out the following problem, and am hoping that someone with greater experience will know the answer.
Symptom : water flows from the cold storage cistern warning pipe
system : open vented, fully pumped, S plan
boiler : gas, some kind of Potterton
MZVs : Honeywell 2-port, 2 off
roomstat : on 21 degC
cylinder stat : on 60 degC
programmer : can't remember, but it's a two-channel digital unit
vent : clear
One outlet from the cistern is the cold feed to the cylinder, in 22mm.
Another outlet, slightly higher, is to the cold side of a Stuart Turner twin impeller pump.
The cistern was renewed in July 2005 - was 20g, now 50g.
The symptom appeared in November.
The system is slightly unusual in that all hot water is pumped (I suspect that the wrong kind of mixer taps were chosen, with the bathroom cold being fed from the mains).
My observations are as follows:
1. The water level in the CSS gradually rises, over a few hours (according to the customer), until it overflows down the warning pipe.
2. The water in the CSS is distinctly warm - not measured, but around body temperature.
3. With a strong torch, I can see subtle signs of heated water emerging into the cistern from one of outlets - the one that goes to the cylinder.
4. The F&E cistern contains stagnant water, implying that the primary circuit doesn't leak water to anywhere.
5. The float valve shuts off nicely, and I've seen that the water level still rises.
So, heated water is rising up the cold feed. I don't know why. The cistern water is therefore at an unhealthy temperature. Also, because the water expands, the level rises and runs out of the warning pipe, irritating the customer.
I'm tempted to fit a single check valve, but there's a risk of it blocking which would starve the pump. So I'd like to find the cause and stop it happening, but I'm stuck.
Has anyone seen anything like this?
Today, I are mostly a punter: I can't figure out the following problem, and am hoping that someone with greater experience will know the answer.
Symptom : water flows from the cold storage cistern warning pipe
system : open vented, fully pumped, S plan
boiler : gas, some kind of Potterton
MZVs : Honeywell 2-port, 2 off
roomstat : on 21 degC
cylinder stat : on 60 degC
programmer : can't remember, but it's a two-channel digital unit
vent : clear
One outlet from the cistern is the cold feed to the cylinder, in 22mm.
Another outlet, slightly higher, is to the cold side of a Stuart Turner twin impeller pump.
The cistern was renewed in July 2005 - was 20g, now 50g.
The symptom appeared in November.
The system is slightly unusual in that all hot water is pumped (I suspect that the wrong kind of mixer taps were chosen, with the bathroom cold being fed from the mains).
My observations are as follows:
1. The water level in the CSS gradually rises, over a few hours (according to the customer), until it overflows down the warning pipe.
2. The water in the CSS is distinctly warm - not measured, but around body temperature.
3. With a strong torch, I can see subtle signs of heated water emerging into the cistern from one of outlets - the one that goes to the cylinder.
4. The F&E cistern contains stagnant water, implying that the primary circuit doesn't leak water to anywhere.
5. The float valve shuts off nicely, and I've seen that the water level still rises.
So, heated water is rising up the cold feed. I don't know why. The cistern water is therefore at an unhealthy temperature. Also, because the water expands, the level rises and runs out of the warning pipe, irritating the customer.
I'm tempted to fit a single check valve, but there's a risk of it blocking which would starve the pump. So I'd like to find the cause and stop it happening, but I'm stuck.
Has anyone seen anything like this?