lighting circuits and cooker circuit code 2 or code 4 on a periodic, its a domestic house thanks 
lighting circuits and cooker circuit code 2 or code 4 on a periodic, its a domestic house thanks![]()
when you say outside appliances do you mean gardening appliances ect?![]()
The "outside appliances" factor is now completely irrelevant - that's no longer in the regulations.Normally code 4, however something you should consider is if the cooker panel has a socket outlet, and it is deemed as possible to be used for appliances outside, then that would be a 2.
The "outside appliances" factor is now completely irrelevant - that's no longer in the regulations.
411.3.3 Additional protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(i) socket-outlets with a rated current not exceeding 20A that are for use by ordinary persons and are intended for general use, and
(ii) mobile equipment with a current rating not exceeding 32A for use outdoors.
An exception to (i) is permitted for:
(a) socket-outlets for use under the supervision of skilled or instructed persons, e.g. in some commercial or industrial locations, or
(b) a specific labeled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
Sorry - what I meant was that 471-16-01 has not been carried over into the 17th. The default is that all BS 1363 sockets are required to have RCD protection, even those in flats 100 floors up.er... beg to differ there BAS..