Picture Of The Week (With A Nod To RF...)
11 Jan 2004
Two pictures: spot as many mistakes as you can.
An installation outside in my local precinct:
A domestic cutout:
theiving gits :x ! and as it is old colors, the blue should be black, that is L3 as far as anyones concerned. Exposed neutral block as well- doesn't really matter but incase of a fault it could become live. And why have 4 earth wires coming out of the cutout? it should of had an earth block installed.
I've seen DNO supplies installed like that before. It might be feeding a second cutout, but they would have more likely used split con rather than SWA. :roll:
It's hard to tell. I think so. The timer (I think) is being fed from the FCU, not vice versa and because the timer is DI, they have not taken a cpc to it.
I think the spur feeds the timer with a L+N then a third wire (switched feed) heads back to the spur to connect to the outgoing lives (I guess those T+E cables).
The yellow core of that SWA isn't connected to the PME terminal, doesn't look like the armour is either. (I'm assuming its PME - may be an assumption too far!)
Can't see the first one too well but as for the second one:
Exposed live conductors
Earth cable not G&Y (well, i'm presuming its an earthing/bonding conductor)
Mixing of old and new colours
Dno equipment being used as MET
Undersized 'tails (and is that blue one smaller than the red? - 10mm? :shock: )
awaiting corrections and additions!