Have looked at your problem. To me it would appear there is nothing wrong with programmer or the room stat.
The problem is the 3port mid position valve.
It could just be stiff and too much resistance for the motor to drive the valve over the second half.
Test by removing the head from the spindle and try turning spindle with fingers.
If the valve spindle is free. The fault relates to the actuator head.
It could be a wiring problem or if it has worked OK, it's most likely a microswitch problem..
There are two microswitchs, each with two pairs of contacts cover four functions.
The functions include
Supply power to drive motor over first half of range
Supply power to drive motor over second half of range
Supply power out from valve to boiler/pump.
It could be the valve moves to the CH position, 2nd microswitch at fault would stop boiler from operating.
It could the valve will not go beyond mid position. This being due t 1sr microswitch problem..
So first check valve for stiffness, Then verify wiring is in order and finally replace the actuator head.
Note 5 wires
White room stat to valve
Grey. HW off to valve
Orange. Valve to boiler/pump
Blue Valve to Neutral
Green/yellow. Valve to earth
The problem is the 3port mid position valve.
It could just be stiff and too much resistance for the motor to drive the valve over the second half.
Test by removing the head from the spindle and try turning spindle with fingers.
If the valve spindle is free. The fault relates to the actuator head.
It could be a wiring problem or if it has worked OK, it's most likely a microswitch problem..
There are two microswitchs, each with two pairs of contacts cover four functions.
The functions include
Supply power to drive motor over first half of range
Supply power to drive motor over second half of range
Supply power out from valve to boiler/pump.
It could be the valve moves to the CH position, 2nd microswitch at fault would stop boiler from operating.
It could the valve will not go beyond mid position. This being due t 1sr microswitch problem..
So first check valve for stiffness, Then verify wiring is in order and finally replace the actuator head.
Note 5 wires
White room stat to valve
Grey. HW off to valve
Orange. Valve to boiler/pump
Blue Valve to Neutral
Green/yellow. Valve to earth