- Joined
- 27 Jan 2008
- Messages
- 29,812
- Reaction score
- 3,696
- Location
- Llanfair Caereinion, Nr Welshpool
- Country
If test current is to earth, it actually proves there is an earth to start with.Seems odd they'd be configured that way
Would have thought keep current on the live conductors
In the consumer unit we can near enough guarantee there is an earth, and the volt drop is low enough for the device to work.
But at the socket, we want to be sure enough power to work the device, and that the earth is there.
Often we rely on a socket RCD, as there is no overload which would work within the required time, this is the case with my RCD sockets, the 5 kW inverter feeding the sockets could never supply even enough power to trip a 10 amp MCB on the magnetic part of the trip, 5 kW at 230 volts = 21.8 amps, and a type B10 MCB needs 50 amps to trip the magnetic part of the trip, and the thermal part is too slow.
And if we have a load of 52 amps (13 amps x 4 outlets) the inverter will likely lock out, but as to how it would react between 21.8 and 52 amps, I simply don't know, I have had generators which with a rapid load applied have dropped voltage, so the overload has failed to open, and that is why we fit active RCDs so if the voltage drops they fail-safe.
These scenarios do not really apply here, but it does explain why the test is to earth.
So no more than 50 volts AC to earth, so at 30 mA at 50 volts it must trip, 50/0.03 = 1667Ω and 254/1667Ω = 152 mA so to ensure even at 50 volts it will trip it means it will also trip the device even if it needs 152 mA to trip it, so it is unlikely to detect when DC is causing the device to need more current to trip.
It is possible it only allows for a volt drop to 200 volts, so looking at 40 mA, but it is unlikely the test button only allows 30 mA to flow, so it is only to check the mechanism has not stuck.
It also seems that reverse current flow, will cause damage to a mono-directional RCD when the test button is pressed, I don't have money to throw away testing if they burn out if a RCD tester is used.
So we are looking at someone else's money, it is all well and good, as I have done, making a risk assessment with ones own home, to decide if the type AC RCD should be replaced with a type A, and I have only fitted type A where a socket on that circuit may be used to charge my son's EV. I have assessed the risk, and I feel the chance of a fault to earth accruing at the same time as some appliance has also allowed DC to flow, with 14 RCBOs in the board is very low, so I still have 12 type AC RCBOs in the board.charity building
I would think not domestic, so in real terms only someone who is trained should touch the electrics, I know with the heritage railway I work on, my qualifications had to be viewed and photo of them kept on record, most volunteers are not allowed to touch electrics.
There is a register kept as to skills, be it using a grinder or a cash till, records have to be kept, including any tool box talks attended, not to do this is like a red flag to a train, everything stops.
So if an electrician says xyz is not safe, and we all think it is safe, then the electrician who counters the order, would need to be trained to a higher level.
So in this case, the installers would need to return and fix it. Or someone else would need to fix it. Not looking at if dangerous or not, I am looking at who could countermand the decision of the EICR inspector.
If there is a clear fault, then fixing it is the way forward, it only requires a minor works certificate raising to show work has been done.
Where the problem lies is where there is no real fault, can't fix something which does not need fixing, and also if no real fault found, how does the second guy know it is not something he has missed?