programable room stat and y plan

Joined
4 Jan 2009
Messages
47
Reaction score
4
Location
Manchester
Country
United Kingdom
Hi all
Wonder if anyone could give me some advice? How would you wire a programmable room stat with y plan set up. Would i have to keep programmer and wire com on stat in series with central heating on on programmer and n/o on stat to white on mid position valve? the only problem is that would have to have ch on programmer on all the time. or is there another way of by passing programmer? cheers
 
Sponsored Links
Simply connect the rf stat to the same points as the current stat.
You will have to keep the timer to ch constant, as you cannot remove the timer due to the dhw needs.
 
If you want to bypass the CH side of the old programmer, just move the wire from the CH ON terminal to the L terminal of the old programmer. If you are installing a wireless programmable stat you will also need a neutral; you may have this already on your old stat.
 
Sponsored Links

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top