Bonding of gas and water supplies is not done to improve the electrical earth. It may do this, but it is really the other way round. It is done to make sure the supplies are at the same voltage as the electrical earth system. Connecting an earth rod directly to the water supply where it enters the house would actually make matters worse.
The electrical earth should have its own dedicated method of connecting it to the outside world earth. Here this seems to be by connecting it to the cable sheath coming in. That is how it is intended to work, and should be fine. There is one point alongside where your electrical supply comes in which is the official reference earth for the whole house.
The argument above is about whether the connections to the sheath are good enough. It is not just a question of resistance across the joint, but also current carrying capacity if there was a fault. The middle of a big short circuit would not be a good time to discover that the lead clamp was the weak point acting as fuse.
If you look at the footnotes to table 7.1 in the OSG, you will see it states cable lengths are based upon voltage drop unless otherwise marked. For the rings listed, it is not immediately obvious what the lengths are based on as they mostly have different footnotes. I think the table is calculated to give you worst-case safe lengths, without having to do explicit calculations of things which might allow you to have a longer cable.
A type 2 mcb is a now obsolete standard about how much current is needed to operate the breaker. You would now expect to use a type B, which gives the much happier length of 88m rather than 58m for 30A ring. Possibly you would use a type C for lighting, but not otherwise.
The question of whether you have or need an rcd does not affect your choice of a type B. Any short circuit between neutral and live will operate the mcb. A short between earth and live will operate the mcb provided the earth is good enough. The question of what supply youy have and how good an earth it provides applies here. If the earth is not good enough, then you have to use an RCD. You may have an RCD anyway, even where it is not absolutely required, because it should operate faster and trap very small shorts to earth.