As above - I was having a mix of F1's and F0's (no pressure) and after replacing a badly leaking water flow/pressure sensor with the new versions and cleaning up the mountings on that and the drain valve which were leaking in the brass threads (cleaned up and fitted back with ptfe tape - all water tight now) the F0's seem to have gone away.
However the F1's have got worse and I have bridged the overheat thermostat which I had replaced, just to confirm it's not the overheat thermostat and it still does it with the overheat thermostat bridged out, sometimes 2 or 3 times a day. Quite often if you have been turning the hot tap on and off, ie firing up and shutting down the boiler.
The boiler always lights first click and the flame is perfect. It has a single probe on the left side which I noticed is 'L' shaped and is set about 1mm above the metal burner outlets, maybe even touching them. Barely half a millimeter of gas flame gets under the probe - could this be the problem? It's 6 years old, should I get a new one if this is likely to be the problem and if so how far into the flame/how do you set the probe up?
Anything else that could be causing the F1 failure? Had a spate of stuff with this otherwise clean and shiny boiler and really want to get to the bottom of it, now the leak and the pressure switch and the overheat thermostat are sorted it's annoying me I now have this problem.
Help appreciated,
Greg.
Help appreciated,
Greg.