1500W at 12V240V would equate to a current of 12.76A (near enough to 13A!) with a PF of 0.49, but the "efficiency" would then have to be 100% for the current to be 12.76A if the "product of efficiency and PF" were 0.49. To get 13A with a "product of efficiency and PF" of 0.49 would require the "efficiency" to be about 101.9%.
Ah - thanks. Now corrected. Not so much a typo as a brain malfunction - even my fingers are unlikely to type "12" when they have been told to type "240"
Thanks everyone. Have located a 16A MCB on ebay, so hopefully sorted tomorrow. My electrician will be fitting it. But I'd like to ask... is changing this MCB for one with a higher threshold notifiable in Wales? Would a series of tests nomally be carried out after the exchange?
Ta
OK - but that's a rather odd quantity ....
1500W at 12V240V would equate to a current of 12.76A (near enough to 13A!) with a PF of 0.49, but the "efficiency" would then have to be 100% for the current to be 12.76A if the "product of efficiency and PF" were 0.49. To get 13A with a "product of efficiency and PF" of 0.49 would require the "efficiency" to be about 101.9%.
I don't, and on the basis of what I told you, it clearly isn't (unless 'efficiency' is exactly 100%).
What I was saying was that IF the PF were 0.49, then 1500W at 240V would equate to a current of 12.76A (near enough to your 13A) - and I could have added, for clarity, that to get exactly your 13A figure, PF would have to be about 0.48 (more precisely, about 0.4808).
You tell us that the "product of efficiency and PF" is 0.49 and that results in the current being 13A. Since, as above, the get 13A would require a PF of about 0.4808, if the "product of efficiency and PF" were 0.49, that would mean that 'efficiency would (as I wrote before) have to be about 1.019 (0.49 / 0.4808) - i.e. an 'efficiency' of about 101.9%.
Good question, and it really depends upon how one interprets the word "replace". In Wales, "replacing any fixed electrical equipment" is not notifiable provided that it does not involve the provision of new fixed cabling or a new CU. Whether 'replace' includes changing an MCB for one of different rating, I don't know. On the face of it, it would seem a little unlikely that they intended that one could change all the MCBs in a CU to ones of different ratings without notification, but I really don't know.
I was told if the breaker is changed for one of different values, it makes the circuit a "new" circuit and strictly speaking an EIC should be produced just for that circuit.
When I changed the dodgy Wylex breakers, I just did a MWC, with IR & Zs.
I was told if the breaker is changed for one of different values, it makes the circuit a "new" circuit and strictly speaking an EIC should be produced just for that circuit.
Yes, I would think that a change of OPD rating probably warrants an EIC (and the associated testing), but that is somewhat different from the OP's question about notifiability (in Wales).
One obvious thing about changing the rating of an OPD (particularly an 'upwards' change) is that it involves 'design' decisions, and the impression I get is that the intention in Wales (as previously in England) is that that none of the things allowed without notification really involve any design issues. I therefore remain uncertain about the notifiability (in Wales). Do you have any thoughts?
In England, now, it would presumably not be notifiable. If one changed all the OPD's then that might be getting rather close to 'replacing the CU', but I can't see that changing just one would come into that category.
Fair enough, but I think it was fairly clear that my comment "I'll be interested to hear what others think." related to the OP's question about notifiability (in Wales) - particularly given that it followed immediately after my "...I don't know" and "...I really don't know" in relation to the notifiability question!
I would think it should be notifiable as it could make the installation less safe and non-compliant if testing is not possible because of lack of knowledge or equipment.
However, it must surely come under - or rather NOT come under and hence NOT be notifiable - the following:
then there is (c)
but you are not refixing or replacing enclosures - or are you?
I would think it should be notifiable as it could make the installation less safe and non-compliant if testing is not possible because of lack of knowledge or equipment.
That's what I referred to - but, as I said, it really depends upon the (undefined) meaning of "replace". As above, I agree with you that one would have thought 'replacing' an OPD with one of higher rating 'should' be notifiable. As I also said, I do start wondering when I think about the fact that, using your argument, one could theoretically change all the OPDs in a CU for ones of different ratings without notification - and I find it hard to believe that whoever wrote it intended that such would not be notifiable...
... so, if changing multiple OPDs for ones of different ratings were (should be) notifiable, that might also apply to changing the rating of just one.
Yet again, a problem of absent definitions. I know we all scorn mention of 'like for like replacement' (since the rules don't mention that anywhere) - but this is one situation in which it would be nice to know whether or not they regard changing an OPD for one of different rating as being just a 'replacement'.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local