pump permanently running

Joined
14 Oct 2008
Messages
995
Reaction score
13
Location
Surrey
Country
United Kingdom
The pump has decided to run 24hr even with programmer set to HW and CH off. The boiler is a potterton suprima and I have two 2 port valves, what d'ya think lads?
 
I think you haven't yet checked to see if one of the motorised valves is stuck open.
 
one of the valves is faulty, possibly the heating valve.

Just had the exact same problem this morning
 
That's weird, came home from work to test the valves as you suggested (both made wirring noises when activated by programmer) let the hot water heat up for an hour and now the pump is shutting off correctly. I've been on holiday for 10 days, do you think that one of the valves might have got slightly seized? both valves are mounted in vertically running pipes
 
could be an intermittently sticking valve, the pipes and boiler will all be hot if that's the case or it could be a faulty pcb as it has a pump live so will power the pump.
 