Query about Central Heating Pump

Joined
23 Sep 2006
Messages
8
Reaction score
0
Country
United Kingdom
I have recently moved house that has LPG Gas central heating and noticed my Leccy bill is quite high for one months usage. The pump that runs my system is WPS make and there are three settings, it was set at number 3 what difference would it make if i moved it to setting number 2. I'm new to this type of heating and every bit of help would be much appreciated.
Cheers the noo
 
Sponsored Links
If it needs to be on 3 and you turn it down you'll get cold and your boiler will get hot.
They're mostly only about 120W flat out, but we don't know the model or the system.....
 
Thanks for the reply the gas boiler is a Myson Appollo 14 year old since new and the Pump has WSP GOLD on it, hope that helps.
 
To add to my last post can anyone tell me what the 3 settings on the central heating pump signify.
 
Sponsored Links
Apollo is a low water content boiler and pump needs to be on speed 3 to clear the heat otherwise boiler will get noisy
 
if the CH pump is 120W max, and you pay, say, 10p per kWh, it will cost about 10p for 8 hours (say, a day's worth)

A 12W energy-saving light bulb will ruin for 80 hours for 10p (about 2 weeks typical usage)

Your tumble drier, however, will run for about 24 minutes for 10p.

To cut electricity usage, start with heating devices.
 
24 minutes for 2.15p

But I don't know about LPG
 
Thanks namsag if it needs to be on 3 then thats my query solved. Many thanks everyone
 