If you add sockets to an existing circuit protected by ACs, does the latest amendment of the regs mandate swapping them to As?
 
Ask Ai.
I tried and gave a extensive answer.
 
Depends what the sockets for I suppose.

I recently put some sockets in a garden office from a split load board I replaced the rcd the new circuit was on from type AC rcd to type A.

So I will do it from now on.
 
So id say yes as who knows what will be plugged in.

Screenshot_20261027_082957_Chrome.jpg
 
Ah but what about an empty property where the loads are unknown?

That's easy - the answer is in the question.

If the loads are unknown then it is not known that the load currents contain no DC components.

1793132042869.png
 
So, shall we assume unless we "know" otherwise that any socket might be or even has some likelihood of being used with with other loads?

I think the answer might be yes there change to type A.

In our own living installtion we might have a good idea that we do know.
In someone elses installtion we can, at best, only assume which is not to "know" ?
 
I got a new CU fitted some years back, the rcbo box clearly marked type B but the icon was for type AC but did not see that until after it was fitted, clearly it should have said curve B not type B.

However in the real world does it really matter? Unless some auto disconnect device is fitted 6 mA is so small, hard to even measure, and most old radios, and TVs would allow some DC, as would the simple three port valve.

So only real way is to limit how much is connected to each RCD so any malfunction has a limited effect.
 
What does this mean?

1793366223994.png


Does it mean that the only things a Type AC should serve is fixed equipment where it is known that the load current contains no DC components?

Or does it mean that if serving fixed equipment that equipment should have a load current containing no DC components?
 
And are we talking about under normal conditions or fault conditions. Most electronics should not produce DC components under normal conditions but could well develop faults that involve DC components.
 