I have CH system to balance.

I have read the FAQ's for further help.

The standard advice is to open all rads to 1/4 turn.

Why don't you open the rads fully, and wind back to balance, if necessary?

Cheers for any help.
 
Sponsored Links
The idea is to get at least some flow to all of the radiators initially.

With all of them wide open, it's likely some wouldn't heat up at all.
 
The standard advice is to open all rads to 1/4 turn.

Why don't you open the rads fully, and wind back to balance, if necessary?
Two reasons:

1. The typical lockshield valve is full open at about 1 to 1½ turns from closed. As many LS valves can open over two turns from closed you will have to wind the LS valve in over a turn before it starts to have the slightest effect.

2. A quarter turn open is much closer to the required setting.

Don't forget that a 15mm pipe can carry about 6kW at a 11C differential, so if you are connecting a 1kW rad to 15mm pipe you need to reduce the flow rate to 1/6th of the open flow rate.
 
Sponsored Links
There is another reason.

Bit more difficult to explain though.

If the valves are well closed then the pump pressure will be higher.

A higher pump pressure will better send more flow through the highest resistance circuit.

In practice setting to just open 1/4 turn is very close to a reasonable setting and an installer could bit a boiler, commission it and then leave it working for a day or two and come back to do the final balancing having left a reasonably well working system.
 