• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

radial circuit

Joined
26 Jan 2006
Messages
7
Reaction score
0
Location
Dorset
Country
United Kingdom
ive just noticed i have a 2.5 t&e radial circuit in the bedroom (old extension) that has 3 double sockets on it and total lenth from the cu is about 12mtrs . is this acceptable and if so what mcb should be used .
 
It is considered acceptable to supply an area not exceeding 50m² with this arrangement, a 20A MCB is normally used. (16A MCB is also acceptable).
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top