I want to run two 2.5 T+E radial circuits from the same 20amp mcb in the cu What is the max length these can be
The Cu is in a Garage
 
Sponsored Links
You shouldn't bunch circuits on breakers.

wire only one radial or wire as a ring would be a better option
 
Sponsored Links
I want to run two 2.5 T+E radial circuits from the same 20amp mcb in the cu What is the max length these can be
The Cu is in a Garage

Read 314.1 to 314.4 of BS7671 and page 363 of same.
 