ive just noticed i have a 2.5 t&e radial circuit in the bedroom (old extension) that has 3 double sockets on it and total lenth from the cu is about 12mtrs . is this acceptable and if so what mcb should be used .
 
Sponsored Links
It is considered acceptable to supply an area not exceeding 50m² with this arrangement, a 20A MCB is normally used. (16A MCB is also acceptable).
 