Radiator mean temperature

Do you know the total installed output of your rads in Btu/hr or kW or the number of double and single rads, have theyTRVs?.
I think you said the minimum output of your boiler is 6.9kW?
 
At what boiler flow temperatures is best to balance at please?
I would agree that the balancing should be done at a dT of 20C, but only at a high boiler flowtemp of say 75C, any small error of up to say 0.5C in measuring the return won't then have a huge effect overall in balancing. You can see quite clearly in the spreadsheet that as the boiler flowtemp is reduced, so too is the dT and the important bit, the return temperature will also reduce and get into condensing territory pretty fast. You can also get a good indication from the spreadsheet of the minimum target (SP) boiler flowtemp you should set to avoid boiler cycling.
If the total installed rad output is say 17kW then assuming a minimum boiler output of 6.6kW means a minimum boilerflow SP of ~ 48C which results in a returntemp of ~ 39C, well into condensing terrority, the dT is then "only" 8C but is of no importance really.
 

Attachments

Do you know the total installed output of your rads in Btu/hr or kW or the number of double and single rads, have theyTRVs?.
I think you said the minimum output of your boiler is 6.9kW?
9.3 kw 7 rads ( 4 x type 22s 1.5, 1.5, 2, 2 kw ) (2 x 0.6 kw small type 21's) ( 1 x 0.8 kw single fin in hallway), 1 towel rad 0.4 kw,
Yes minimum 6.9 kw, only 1 room struggles with lower (55c) temperatures, a bedroom with a 0.6 kw but that's not really a problem, plus I'm going to increase the loft insulation above it anyway.
 
I would agree that the balancing should be done at a dT of 20C, but only at a high boiler flowtemp of say 75C, any small error of up to say 0.5C in measuring the return won't then have a huge effect overall in balancing. You can see quite clearly in the spreadsheet that as the boiler flowtemp is reduced, so too is the dT and the important bit, the return temperature will also reduce and get into condensing territory pretty fast. You can also get a good indication from the spreadsheet of the minimum target (SP) boiler flowtemp you should set to avoid boiler cycling.
If the total installed rad output is say 17kW then assuming a minimum boiler output of 6.6kW means a minimum boilerflow SP of ~ 48C which results in a returntemp of ~ 39C, well into condensing terrority, the dT is then "only" 8C but is of no importance really.
What if I wanted to balance at a flow temp of 55c, what Delta should I go for? 10/12c?
 
What if I wanted to balance at a flow temp of 55c, what Delta should I go for? 10/12c?
If you run with a flowtemp of 55C and a dT of 5C, "9.3kW" rads will only output 5.31kW so the boiler will cycle frequently and you havn't a hope of balancing at that temperature, even worse, if, by some chance the dT was 10C, the output then falls to 4.8kW. The very best you will get is 5.53kW at a dT of 3C, (with a flowtemp of 55C).
To get the boiler running continuously with a dT of 10C you will have to balance at a flowtemp of 65C (+10C dT) which gives a output of almost 7.0kW.
At Flowtemp/dT of 70C/10C, the boiler output is 8.1kW, comfortably above the minimum output of 6.9kW.

Attached is a spreadsheet for a system balanced to 10C at a Boiler Flowtemp of 70C.
 

Attachments

Last edited:
On your last question: 10 to 12°C at a 55°C flow temperature is fine for a condensing boiler, and you don't need to redo it for every flow temperature. Balancing only sets how the water is shared between the radiators, and that share stays about right when you turn the boiler down.

Where I'd differ from Johntheo5 is going up to 65 or 70°C to keep the burner lit. His figures are useful the other way round: if the house stays warm at 55°C, it is getting by on about 5 kW or less, and your boiler can't go below 6.9 kW. So it will stop and start on most days whatever you balance to. Hotter water doesn't change what the house needs, it only moves the stopping to the room stat and costs you the condensing. What does help: every radiator open in the rooms you use, long steady heating periods instead of one-hour boosts, and, if the 30si has them (the installer manual will say), a lower maximum heating output and a longer anti-cycle time.

Was the balancing worth it? For me it was. When I was still on gas, turning the flow temperature down and balancing so each radiator gave what its room loses roughly halved my bill, with every room at temperature. The saving comes from the lower flow temperature, the balancing is what lets every room cope with it.

That is where your one bedroom comes in: its 0.6 kW radiator decides how low the whole house can go. A heat loss figure for that room, before and after the loft insulation, tells you whether the insulation is enough or it wants a bigger radiator. I worked mine out room by room not long ago, this is what that looks like: https://heatlosspro.cloud/s/YAzppFumRwF3TzRGRBaV0g
 