Think your overthinking it all.
KISS
Keep it simple stupid
KISS
Keep it simple stupid
I agree, maybe I amThink your overthinking it all.
KISS
Keep it simple stupid
I would agree that the balancing should be done at a dT of 20C, but only at a high boiler flowtemp of say 75C, any small error of up to say 0.5C in measuring the return won't then have a huge effect overall in balancing. You can see quite clearly in the spreadsheet that as the boiler flowtemp is reduced, so too is the dT and the important bit, the return temperature will also reduce and get into condensing territory pretty fast. You can also get a good indication from the spreadsheet of the minimum target (SP) boiler flowtemp you should set to avoid boiler cycling.At what boiler flow temperatures is best to balance at please?
9.3 kw 7 rads ( 4 x type 22s 1.5, 1.5, 2, 2 kw ) (2 x 0.6 kw small type 21's) ( 1 x 0.8 kw single fin in hallway), 1 towel rad 0.4 kw,Do you know the total installed output of your rads in Btu/hr or kW or the number of double and single rads, have theyTRVs?.
I think you said the minimum output of your boiler is 6.9kW?
What if I wanted to balance at a flow temp of 55c, what Delta should I go for? 10/12c?I would agree that the balancing should be done at a dT of 20C, but only at a high boiler flowtemp of say 75C, any small error of up to say 0.5C in measuring the return won't then have a huge effect overall in balancing. You can see quite clearly in the spreadsheet that as the boiler flowtemp is reduced, so too is the dT and the important bit, the return temperature will also reduce and get into condensing territory pretty fast. You can also get a good indication from the spreadsheet of the minimum target (SP) boiler flowtemp you should set to avoid boiler cycling.
If the total installed rad output is say 17kW then assuming a minimum boiler output of 6.6kW means a minimum boilerflow SP of ~ 48C which results in a returntemp of ~ 39C, well into condensing terrority, the dT is then "only" 8C but is of no importance really.
Yes I realise that, thanksJohnytuono.
That was not meant as a insult to you, just a expression
If you run with a flowtemp of 55C and a dT of 5C, "9.3kW" rads will only output 5.31kW so the boiler will cycle frequently and you havn't a hope of balancing at that temperature, even worse, if, by some chance the dT was 10C, the output then falls to 4.8kW. The very best you will get is 5.53kW at a dT of 3C, (with a flowtemp of 55C).What if I wanted to balance at a flow temp of 55c, what Delta should I go for? 10/12c?