rcbo

Joined
16 Jul 2007
Messages
19
Reaction score
0
Country
United Kingdom
are they a straight swap(assuming you have the correct type for your cu) thanks in advance ,jim
 
Fairly streight forwards, if they are single width they are usually a bit taller than an MCB. 2 module width ones are usually same height as an MCB. As with all RCDs they will require circuit neutrals to be diverted through them, they usually come with a flying lead to connect to the neutral busbar.
 
Spark123 said:
Fairly streight forwards, if they are single width they are usually a bit taller than an MCB. 2 module width ones are usually same height as an MCB. As with all RCDs they will require circuit neutrals to be diverted through them, they usually come with a flying lead to connect to the neutral busbar.

Thanks spark123, its a single width wylex one (no cheap either £35 :cry: )jim
 
bigjim12 said:
Spark123 said:
Fairly streight forwards, if they are single width they are usually a bit taller than an MCB. 2 module width ones are usually same height as an MCB. As with all RCDs they will require circuit neutrals to be diverted through them, they usually come with a flying lead to connect to the neutral busbar.

Thanks spark123, its a single width wylex one (no cheap either £35 :cry: )jim

I've just fitted one in place of an MCB. The live wires are pretty much as they were in the MCB. The neutrals that used to go to the bar now go to the RCBO instead and the neutral wire from the RCBO goes to where the neutrals used to be. And there's an earth cable to connect also.
 
Just a note. Under some circumstances single pole RCBO's are not suitable for protection on TT systems so you do need to check you earthing arrangements.
 
Pensdown said:
Just a note. Under some circumstances single pole RCBO's are not suitable for protection on TT systems so you do need to check you earthing arrangements.
My supply is 100amp wylex fuse box ,the earth goes under the ground (where to ?good :?: )no cables overhead entering the building,so will my rcbo be ok,cheers again ,jim
 
ricicle said:
Pensdown said:
Just a note. Under some circumstances single pole RCBO's are not suitable for protection on TT systems so you do need to check you earthing arrangements.

:?

Yeah, you've got me interested as well pensdown!, any chance of any more detail?
 