Hi all, I am part way through installing/testing a new consumer unit (going back tomorrow to complete the testing)
Ground floor ring (2.5mm wire, 32amp MCB, Crabtree 30ma RCD)
RCD test does not trip the RCD at 1X, 180 deg (negative half cycle)
All other RCD tests are good including the 5X which trips in 23ms on 0 deg and 17ms on 180 deg. 1X, 0 deg is also good at 43ms.
I had to leave the site so I could not do any further investigations this evening but just wanted to get a head start on it for tomorrow. Do you think this could be related to capacitance in the circuit? As I write this I start to think that the boiler (combi) may be wired to a spur off this ring..... Could it be filter capacitance in the combi? But the 5X test works well... any ideas would be very much appreciated.
I'm using a Seaward PowerTest 1557, well inside calibration date and worked well last week on two smilar jobs.
Thanks, I'm new to this forum and there looks to be a lot of very good info and some smart people too (smart in the academic sense, don't know about your dress sense)
Ground floor ring (2.5mm wire, 32amp MCB, Crabtree 30ma RCD)
RCD test does not trip the RCD at 1X, 180 deg (negative half cycle)
All other RCD tests are good including the 5X which trips in 23ms on 0 deg and 17ms on 180 deg. 1X, 0 deg is also good at 43ms.
I had to leave the site so I could not do any further investigations this evening but just wanted to get a head start on it for tomorrow. Do you think this could be related to capacitance in the circuit? As I write this I start to think that the boiler (combi) may be wired to a spur off this ring..... Could it be filter capacitance in the combi? But the 5X test works well... any ideas would be very much appreciated.
I'm using a Seaward PowerTest 1557, well inside calibration date and worked well last week on two smilar jobs.
Thanks, I'm new to this forum and there looks to be a lot of very good info and some smart people too (smart in the academic sense, don't know about your dress sense)