rcd regs
Simple answer "No" but what it does say
415.1.1 The use of RCDs with a rated residual operating current (I∆n) not exceeding 30 mA and an operating time not exceeding 40 ms at a residual current of 5 I∆n is recognised in a.c. systems as additional protection in the event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users.
Which means if the reason for an RCD is to protect against shock then 30ma or less. For fire 300ma is recommended.
For automatic disconnection of supply because the earth loop impedance is not good enough you have to calculate. Norm was 100ma because of 1/3 rule.
For domestic on consumer unit sockets lights etc.
It's more or less impossible to get away without 30mA RCDs protecting the majority of circuits on a new domestic installation. If you're installing 13A sockets for general use in a domestic setting then you have no choice but to 30mA RCD protect (be it at the CU or the sockets themselves).