Good morning
I was wondering if these questions by council building control for regularisation of a garage to open plan kitchen/diner were easy to answer. My project planner won’t answer them. I have photos of the build that correspond & can PM them if needed….
Any help appreciated
In connection with the photographs provided I have the following comments :-
1. No calculations have been provided for the steel beams installed.
2. Calculations are required for the spliced floor joists and the cut trussed rafters.
3. No restraint straps have been provided the roof/new infill panel.
4. There appears to be non-metallic material between the steel beams and the concrete padstones. Please clarify.
5. In respect of the infill brickwork panel, there is no evidence of a satisfactory foundation below the new wall, a DPC to the inner or outer walls etc.
6. The new windows and doors do not appear to have trickle vents.
7. Please confirm that escape windows are present at first floor level.
8. Please provide the electricians' organisation or governing body's registration number.
9. There appears to be no cross-flow ventilation the roof void over the new room.
10. Please state the thickness of the insulation to the floor, walls and roof space. The insulation to the walls appears to be 50mm thick. Please provide the manufacturers details to confirm the U value of the wall as built.
11. The screws fixing the battens to the walls have pierced the membrane. This will lead to damp penetration. In addition, the IKO Rubershield ECO EXTRA is a breathable roof membrane. Please provide the manufacturers details to confirm that can be used in the position indicated in the photographs.
I was wondering if these questions by council building control for regularisation of a garage to open plan kitchen/diner were easy to answer. My project planner won’t answer them. I have photos of the build that correspond & can PM them if needed….
Any help appreciated
In connection with the photographs provided I have the following comments :-
1. No calculations have been provided for the steel beams installed.
2. Calculations are required for the spliced floor joists and the cut trussed rafters.
3. No restraint straps have been provided the roof/new infill panel.
4. There appears to be non-metallic material between the steel beams and the concrete padstones. Please clarify.
5. In respect of the infill brickwork panel, there is no evidence of a satisfactory foundation below the new wall, a DPC to the inner or outer walls etc.
6. The new windows and doors do not appear to have trickle vents.
7. Please confirm that escape windows are present at first floor level.
8. Please provide the electricians' organisation or governing body's registration number.
9. There appears to be no cross-flow ventilation the roof void over the new room.
10. Please state the thickness of the insulation to the floor, walls and roof space. The insulation to the walls appears to be 50mm thick. Please provide the manufacturers details to confirm the U value of the wall as built.
11. The screws fixing the battens to the walls have pierced the membrane. This will lead to damp penetration. In addition, the IKO Rubershield ECO EXTRA is a breathable roof membrane. Please provide the manufacturers details to confirm that can be used in the position indicated in the photographs.