Indeed - although there is a minimum trip time imposed by such factors as the maximum speed at which the mechanical tripping mechanism can operate .going back a bit, RCDs can trip a little bit faster or slower depending where in the AC cycle contact occurs. Current will be zero momentarily, then increase as the cycle climbs (or falls) towards the next peak. So it may be faster than 30ms
Yep, that's broadly true - but what is your point?I saw this in some tech doc or other, with graphs and timings. It included survivability charts, varying by duration and current, which I don't remember. 30ma for 30ms is mostly survivable. Increase one and unless you decrease the other, survivability falls.
As you will realise, the point I've been making is that a current 'just under 100mA' may, and a current just under 50 mA must, be allowed to flow indefinitely by a 100 mA RCD, whereas a 30 mA RCD will, as it says on the tin, curtail a current >30 mA (and maybe currents as low as ~15 mA) in just a small number of tens of milliseconds (whether 30ms, 40ms or whatever).
So, if body resistance etc. is such that the current through the victim's body is between 30 and 100 mA, a 30 mA RCD must terminate that current very quickly, whereas a 100 mA RCD may not terminate it ever.
Kind Regards, John