Hi, I am trying to replace an analog timer with a Hive, but the timer only has 3 wires. every other discussion I have read mentions 4 wires!

1 (timer) to N (hive)
3 to L
4 to ???
timer-wires.jpeg

Please help!
Thanks
 
Normally the timer is left in place and set to be permanently on 24/7 and the Hive wired to the boilers external terminals provided for a remote thermostat.
 
Normally the timer is left in place and set to be permanently on 24/7 and the Hive wired to the boilers external terminals provided for a remote thermostat.
I don't think there is a connection for a thermostat!
 
I don't think there is a connection for a thermostat!
There will be a connection block within the boiler, that will allow you to connect the thermostat.
Let us know the make and model of the boiler, and we will guide you in the right direction...

A few boiler manufacturers use this same timer.
 
View attachment 297921 Hive is not 48 - 72 volt AC, so can't see how you can replace with Hive without some relays etc.
That is the supply to the motor for the timer.
Theoretically, terminals 1 and 3 of a single channel Hive could be connected to the Black and Blue wires (Red being safely isolated).
The Live and Neutral to power the Hive could be picked up elsewhere.
No need for any additional relays, but using the intended terminal block would be preferable! :)
 
There will be a connection block within the boiler, that will allow you to connect the thermostat.
Let us know the make and model of the boiler, and we will guide you in the right direction...

A few boiler manufacturers use this same timer.
it's a Worcester 24i junior
 

Attachments

  • 20230310_202048.jpg
    20230310_202048.jpg
    299.1 KB · Views: 205
it's a Worcester 24i junior
The connections for an external thermostat are on terminal block 'ST2' (Where the mains flex connects to the boiler PCB):

Screenshot_20230310-204619_Chrome.jpg

Screenshot_20230310-204513_Chrome.jpg


Remove the link between Ls and Lr on boiler.

Assuming a single channel Hive:

Ns to N on Hive
Ls to L
Add a link wire between L and 1 on Hive
Lr to 3 on Hive
 
Last edited:
The connections for an external thermostat are on terminal block 'ST2' (Where the mains flex connects to the boiler PCB):

View attachment 297972
View attachment 297971

Remove the link between Ls and Lr on boiler.

Assuming a single channel Hive:

Ns to N on Hive
Ls to L
Add a link wire between L and 1 on Hive
Lr to 3 on Hive
That was very helpful, thank you!!
What do I do with the timer now? leave it there or disconnect it?
 
Thanks a million guys! This is my first time really using a forum like this and I'm thrilled by the quality of information and speed of reply!
Hive is wired up and working now! The hub is flashing amber for some reason, but I've tun a few tests and it's working the way it should.
Thank you all so much!
20230313_114638.jpg
20230313_114616.jpg
 
Hi again!
Everything was perfect yesterday, but today I have an airflow fault! (Indicator light flashing fast)
I think its making all the right noises, so I hope that means the fan is OK. Gas cooker is working fine, water in taps is fine, should I get on the roof and check there isn't a bird nesting in the chimney!? Or is there anything else I should check before I call a professional?

Pressure looks a bit low, but I thinks it's always been low...

Fingers crossed its only a coincidence that this is the after installing a thermostat...
20230314_085924.jpg
 
Don’t think you need to get on the roof, should be able to see visually if anything blocking the flue. I suspect there‘s an issue with the boiler itself - my advice is get a professional.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top