Replacing 3 gang dimmer with standard switch

Discussion in 'Electrics UK' started by BritishBeef, 25 Jul 2015.

  1. BritishBeef

    BritishBeef

    Joined:
    13 Feb 2007
    Messages:
    95
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi all.
    I have recently had my kitchen moved downstairs (I live in a townhouse) and have mains voltage LED downlights. I bought a Varilight IR V-Pro Trailing Edge dimmer and my Electrician fitted it yesterday. It worked fine for a few hours but now is going haywire and randomly turning on and off by itself!
    Looks like it's faulty but I need lights working in my kitchen now!

    So I have bought a standard 3 gang switch just to get the lights working for now.
    However, after looking at the wiring on my new dimmer and looking at the back of my new switch I'm left confused as to what wires go where. I have successfully wired new switches in the past but have not gone from a dimmer like this to a standard switch.

    Here's a photo of the wired up dimmer switch as it is now:

    [​IMG]
    Not sure if it's clear in the above photo but there is also a grey wire with blue tape on it not connected to anything.

    Here's the rear of the standard switch I want to install instead:

    [​IMG]

    If any of you can help me wire this I would be eternally grateful :)
     
  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    30,200
    Thanks Received:
    3,261
    Location:
    Retired to:
    Country:
    Portugal
    You will note that the new switch has two lines which divide it into three switches.
     
    Last edited: 25 Jul 2015
  4. riveralt

    riveralt

    Joined:
    4 Jan 2004
    Messages:
    4,020
    Thanks Received:
    597
    Country:
    United Kingdom
    Just swap your live and load from the dimmer to Com and L1 for each switch respectively.
     
    Last edited: 25 Jul 2015
  5. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,628
    Thanks Received:
    2,381
    Location:
    Londonderry
    Country:
    United Kingdom
    As above note the way the new plastic switch is divided into three section one for each gang (com L1 L2 x 3) one section is upside down.
    Looking at your picture of the existing dimmer switch, you have 3 perm Lives (1 brown and two red) they are terminated at the com of each gang. Then you have 3 switch lives (black brown sleeve?, black sleeved red, black sleeved yellow), these are then terminated at the L1 terminal of each associated gang.
    So
    Gang 1 Brown to com with black sleeved browm at L1
    Gang 2 Red to com with black sleeved mostly red at L1
    Gang 3 Red to com with black sleeved mosty yellow at L1
    Terminate all the CPCs (earths) to the earth terminal on the backbox
    The grey is left as it is.
    The first black looks like it may have a brown sleeve on, I maybe wrong?
     
    Last edited: 25 Jul 2015
  6. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,711
    Thanks Received:
    1,867
    Location:
    Oxfordshire
    Country:
    United Kingdom
    What he said^^^^

    Re your LED lamps, are they dimmer-able?
    Are all circuits going "haywire" or just one?
     
  7. BritishBeef

    BritishBeef

    Joined:
    13 Feb 2007
    Messages:
    95
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks very much everyone. Works a charm :)
     
  8. BritishBeef

    BritishBeef

    Joined:
    13 Feb 2007
    Messages:
    95
    Thanks Received:
    1
    Country:
    United Kingdom
    The lamps are dimmable yes. It's mainly one of the gangs but the other is doing it too just a lot less frequently. The 3rd gang is conected to a standard light fitting which hasn't got a bulb in so can't test it.
     
  9. Sponsored Links
  10. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    The lights may be dimmable, but do they meet the minimum load requirements of the dimmer?
     
  11. riveralt

    riveralt

    Joined:
    4 Jan 2004
    Messages:
    4,020
    Thanks Received:
    597
    Country:
    United Kingdom
    If you have more than the minimum size load and compatible bulbs then it sounds like the dimmer hasn't been set up properly. Assuming the firmware is 10B or later (the firmware is usually on a sticker on the side of the dimmer module) check the instructions they will show you how to change the mode setting for the problems you are encountering.
     
  12. phatboy

    phatboy

    Joined:
    22 Jan 2012
    Messages:
    1,938
    Thanks Received:
    217
    Location:
    Jersey
    Country:
    United Kingdom
    It may be an illusion, but the Varilight plate looks like 2G, and the plastic one looks like 1G, so is there a big space at one side when you fit it?
     
  13. riveralt

    riveralt

    Joined:
    4 Jan 2004
    Messages:
    4,020
    Thanks Received:
    597
    Country:
    United Kingdom
    It is no illusion, but the OP did state
     
  14. phatboy

    phatboy

    Joined:
    22 Jan 2012
    Messages:
    1,938
    Thanks Received:
    217
    Location:
    Jersey
    Country:
    United Kingdom
    Appreciate it was done in a hurry, but it's not very safe unless some other precaution is taken?

    Standard 3gang doesn't automatically mean a 1g plate though does it?
     
  15. BritishBeef

    BritishBeef

    Joined:
    13 Feb 2007
    Messages:
    95
    Thanks Received:
    1
    Country:
    United Kingdom
    Yes it's not ideal. There is a gap of course but I've tucked all cables behind plate and duck taped over the gap for now. I'm going to buy a 3 gang switch to fit existing back box. There are some available online.
     
  16. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Sponsored Links
Loading...

Share This Page