Replacing Salus RT520TX wireless thermostat with Google Nest

Discussion in 'Plumbing and Central Heating' started by smunir, 14 Oct 2020.

  1. smunir

    smunir

    Joined:
    14 Oct 2020
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    it's a Alpha E-Tec 33 combi boiler.

    We have a Nest 3rd generation thermostat waiting to be installed and I was considering having a go installing it myself but just want to ask opinion on here first then decide whether or not to get a professional to do it.

    There is a fused spur going into the Salus which then goes onto the boiler shown below.
    Will all these cables fit into the Nest? And which slots do the COM & NO wires go into on the Nest?


    My theory is: (Please see the attached images)
    - existing blue/brown wires going into Salus L/N will go into corresponding L/N connectors of the Nest Heat Link
    - single yellow/green wire going into NO/normally-open of Salus will go into connector 3/call-for-heat of Nest Heat Link
    - jumper wire between L and COM/linked-live of Salus needs to be replicated, so put a jumper wire between L and 2/common of Nest Heat Link

    Thanks in advance!
    IMG_0504.JPEG IMG_0506.JPEG
     
  2. Sponsored Links
  3. smunir

    smunir

    Joined:
    14 Oct 2020
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    @stem Can you please advise?
     
  4. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,564
    Thanks Received:
    1,510
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Sounds about right to me:

    Salus N = Nest 3rd gen N

    Salus L = Nest 3rd gen L

    Salus NO = Nest 3rd gen 3 (heating call for heat) Note: It's not good practice to use a green / yellow wire as a live conductor, and as minimum it should have a brown sleeve over it.

    Add a link between Nest 3rd gen L and 2 (heating common)

    If you are going to connect the Nest Thermostat to T1 & T2 to provide it with operating power, the Heat link will also require and earth connection making to the earth terminal to the left of T1

    Provided the Salus was connected correctly to the boiler, there's no need to change any wiring there. If the boiler has integral time control, it needs to be set to be permanently on 24/7.
     
    • Like Like x 1
  5. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page