Folks my girlfriend is getting a kiln with the maximum rated amp at 22A with maximum output of 5KW.
I wanted to ensure that the parts below are all that should be required to connect and meet current standards;
25 meters of 6MM twin+earth cable (over kill but better it be thicker than under?)
1xIP44 angled wall socket (32A 200-250V)
1xIP44 Interlocked straight plug (32A 200-250V)
1xSentry 32A Type B MCB (currently the board is rated at 64A but we have two slots in it with MCB's that are no longer being used)
1xIP65 Isolator switch (again 32A)
Do I need anything else to meet current standards?
(p.s I wont be doing the install a friend will who works for BOC but I wanted to get all the equipment bought ready for him)
Cheers!
Adam.