    Every article I've read, and my onsite guide, shows methods to get through floor joists in the middle of a room. However, I can't find what best practice is when running a cable through the last floor joist before reaching the brick wall, where the gap between the two is only an inch or so.

    Do you drill a hole as normal, then bend the end of the cable a pit so that when you push the cable through it bends round to reach the drop?

    Or is there some other approach?

    Or do you use the safe zone at the top of the wall?

    Or do you just never run sockets on joist-parallel walls?

    Thanks all!
     
  2. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    2,148
    Thanks Received:
    93
    Country:
    United Kingdom
    Creative drilling and a bit of chiselling and yes bend the cable
     
    • Thanks Thanks x 1
  3. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    33,785
    Thanks Received:
    1,030
    Country:
    United Kingdom
    I always had lengths of old solid core bonding cable (uninsulated) which was easy to bend.
    I would thread it through the hole from the side next to the wall then tie the cable on and drag it back.

    A pair of pin-nosed pliers come in handy. Oh, and a pair of gloves too, otherwise scraped knuckles would be a very likely outcome...
     
    • Thanks Thanks x 1
  4. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    2,148
    Thanks Received:
    93
    Country:
    United Kingdom
    A wire coat hanger is a useful tool also
     
  5. Donkmeister

    Donkmeister

    Joined:
    1 Sep 2008
    Messages:
    1,006
    Thanks Received:
    17
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Thanks both, I'll try using a bit of 6mm or 10mm to draw it through.
     
  6. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    31,031
    Thanks Received:
    3,356
    Location:
    Retired to:
    Country:
    Portugal
    Not sure if you meant it literally but you shouldn't run cables "in the middle of the room".
    https://www.diynot.com/wiki/Electrics:route

    Also in OSG, I presume.
     
  7. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    31,031
    Thanks Received:
    3,356
    Location:
    Retired to:
    Country:
    Portugal
    Chisel a notch across the top of the edge joist and cover with a steel plate - as in the link for the copper pipe.
     
  8. Sponsored Links
  9. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    2,148
    Thanks Received:
    93
    Country:
    United Kingdom
    Not sure what you mean?
     
  10. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    31,031
    Thanks Received:
    3,356
    Location:
    Retired to:
    Country:
    Portugal
    upload_2019-4-8_14-46-14.png

    So at 0.5 of the span - i.e. the middle of the room - is not permitted.
     
    • Thanks Thanks x 1
    • Like Like x 1
  11. conny

    conny

    Joined:
    30 Jun 2008
    Messages:
    11,234
    Thanks Received:
    341
    Location:
    Suffolk
    Country:
    United Kingdom
    Depending on the depth of the joist you may be able to drill at a downward angle. i.e. if your joist is 6" deep drill down 2" from the top to within 2" of the bottom. This will give you a lead without having a sharp bend in the cable.
     
  12. Donkmeister

    Donkmeister

    Joined:
    1 Sep 2008
    Messages:
    1,006
    Thanks Received:
    17
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Ah, I mentioned running through joists in the middle of the room, not through the centres of joists.
    I'll be sure to define 3-d axes relative to defined datum points in future to avoid ambiguity ;):p
     
  13. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    31,031
    Thanks Received:
    3,356
    Location:
    Retired to:
    Country:
    Portugal
    How can the middle of the room not be 0.5 of the span?

    The 'centre' of the joist is generally taken to mean half the depth.
     
  14. SimonH2

    SimonH2

    Joined:
    4 Nov 2010
    Messages:
    5,404
    Thanks Received:
    554
    Location:
    Cumbria
    Country:
    United Kingdom
    Colloquially "middle of the room" could be "anywhere but round the outside" - so in this context, anything but the joists close to the walls.
    While the advice above is all sound, there is one thing not mentioned ... That the ****ing ****er ****ard builders often stick the end joists so close to the wall that you can't even see past the skirting. So you end up having to use a fishing rod* at a shallow angle (ie not far off horizontal) to even get it into the gap, and fish blind for the thin pull wire you've pushed through the hole.

    * Aka, cable rods
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Sponsored Links
Loading...

Share This Page