Sanity Check Required - Do I really need 3 Phase Upgrade?

On a slightly related note - when considering diversity for the 4 cookers is it applied:
a) per appliance?
b) per radial/ring they are on?
c) all together regardless of the connection?

Cheers! Phil
 
Sponsored Links
i suppose he could still fit that 3 phase 8way board, balance the load and fit a single phase incomer kit, at least if needbe you could upgrade to 3 phase at a later date.
 
Last edited:
An 8 way TPN board has been specified in his updated quote.
Does this 'electrician' realise that an 8 way TPN board has space for 24 single phase circuits? Nothing in your original list suggested even half that number would be required.
If they are intending to install that many, what price did they quote for the 24 RCBOs?
 
Sponsored Links
Very good point. Just double checked and he has priced for 22 RCBOs at £880.
... which, apart from anything else, clearly begs the question as to what 22 circuits he is planning to install. As has been said, you probably wouldn't need half of that.

Kind Regards, John
 
Only 22? Given the expertise he's shown so far....

  1. 60cm Pyroclean Right Hinged Oven 3.7KW (16A)
  2. 60cm Pyroclean Left Hinged Oven 3.7KW (16A)
  3. Combination Microwave / Oven 3.1KW (16A)
  4. Steam Combi Oven (Reservoir system) 2KW (10A)
    Induction Ring
  5. Induction 5 zone hob 10.8KW (45A)
    Kitchen Ring
  6. Downdraft Extractor 0.3KW
  7. Warming Drawer 0.81KW
  8. Warming Drawer 0.81KW
  9. Fridge Freezer 0.3KW
  10. Wine Cabinet 0.13KW
  11. Dishwasher 2.3KW
  12. Quooker tap 1.6KW
  13. Double Drawer Dishwasher 1.8KW (9A)
    Utililty Room Ring
  14. Washing Machine 2.4KW
  15. Tumble Dryer - Heat Pump 1KW
    Ground Floor Ring
  16. Nothing specific
    First Floor and Loft Ring
  17. Crosswater digital shower valve (not electric shower) .03KW
  18. Spa bath 3.6KW (16A)
    Basement Sump Pump and Alarms
  19. V3 Foul pump 1.2KW (6A)
  20. V3 Sump pump 0.43KW (1.9A)
  21. V3 Sump pump 0.43KW (1.9A)
  22. Alarm unit (2A)
  23. Alarm unit (2A)
    Lights - all LED
  24. Basement 30 @ 10w 300
  25. Ground 30 @ 10w 300
  26. First 30 @ 10w 300
  27. loft 10 @ 10w 100

:mrgreen:
 
On a slightly related note - when considering diversity for the 4 cookers is it applied:
a) per appliance?
b) per radial/ring they are on?
c) all together regardless of the connection?

Cheers! Phil
Unless you want them on separate circuits, add all 4 ovens and the hob, and apply diversity to that.
 
Kitchen cooking appliances 32A
2 ovens, microwave & steam oven

Induction Hob 32A

Other kitchen & utility sockets / appliances 32A

Socket outlets & other fixed items
20A for basement
20A for ground floor
20A for first floor
20A for loft

Lighting
6A
lights basement & first floor
6A lights ground floor & loft


12 way main switch CU with 9 RCBOs for the circuits above and 3 spaces for any future items.
 
3-section CU (or 3 separate CUs), one part connected through a C/O switch to allow local generator to supply CH boiler, some lights and some sockets. Or a separate CU ditto or via a 60309 plug & socket.

One part, or one CU, to allow complete isolation of basement electrics in the event of flooding.
 
Only 22? Given the expertise he's shown so far....

  1. 60cm Pyroclean Right Hinged Oven 3.7KW (16A)
  2. 60cm Pyroclean Left Hinged Oven 3.7KW (16A)
  3. Combination Microwave / Oven 3.1KW (16A)
  4. Steam Combi Oven (Reservoir system) 2KW (10A)
    Induction Ring
  5. Induction 5 zone hob 10.8KW (45A)
    Kitchen Ring
  6. Downdraft Extractor 0.3KW
  7. Warming Drawer 0.81KW
  8. Warming Drawer 0.81KW
  9. Fridge Freezer 0.3KW
  10. Wine Cabinet 0.13KW
  11. Dishwasher 2.3KW
  12. Quooker tap 1.6KW
  13. Double Drawer Dishwasher 1.8KW (9A)
    Utililty Room Ring
  14. Washing Machine 2.4KW
  15. Tumble Dryer - Heat Pump 1KW
    Ground Floor Ring
  16. Nothing specific
    First Floor and Loft Ring
  17. Crosswater digital shower valve (not electric shower) .03KW
  18. Spa bath 3.6KW (16A)
    Basement Sump Pump and Alarms
  19. V3 Foul pump 1.2KW (6A)
  20. V3 Sump pump 0.43KW (1.9A)
  21. V3 Sump pump 0.43KW (1.9A)
  22. Alarm unit (2A)
  23. Alarm unit (2A)
    Lights - all LED
  24. Basement 30 @ 10w 300
  25. Ground 30 @ 10w 300
  26. First 30 @ 10w 300
  27. loft 10 @ 10w 100

:mrgreen:
What's the loading of circuit 16 ?:confused:

DS
 
Think he has made a booboo there, one of many!

It looks like two separate ring finals for GF & FF/Loft.
 
Kitchen cooking appliances 32A
2 ovens, microwave & steam oven

Induction Hob 32A

Other kitchen & utility sockets / appliances 32A

Socket outlets & other fixed items
20A
for basement
20A for ground floor
20A for first floor
20A for loft

Lighting
6A
lights basement & first floor
6A lights ground floor & loft


12 way main switch CU with 9 RCBOs for the circuits above and 3 spaces for any future items.
2 ovens, microwave,& steam oven on a 32a RCBO ? mm, that's a pain in the ass when it trips !

Judging by the kitchen money is not an issue.

Regards,

DS
 
What's the loading of circuit 16 ?:confused:
I presume that, as with many sockets circuits, it is simply "unknown" - so all that can be said is that, unlike the situation for the ground floor and basements, there are no known, or predictable, specific loads which can be cited.

The same would be true of the sockets circuits on the top two floors of my house - apart from pretty trivial things like bedside lights, alarm clocks, a TV or two and electric blankets, I could not cite any other 'likely loads' - although there will undoubtedly be some significant loads plugged in from time to time.

Kind Regards, John
 
2 ovens, microwave,& steam oven on a 32a RCBO ? mm, that's a pain in the ass when it trips ! Judging by the kitchen moneys not an issue.
Yes, I have to say that I might well split it into two circuits, but that still does not get one even remotely close to 22 required final circuits (or a 160A design load for the installation).

Kind Regards, John
 