I am wanting to install a shaver socket into the bathroom and was just wondering what the steps are to do this. much appreciated Tony.
 
Your need to take L,N and E via 1.0mm or 1.5mm twin and earth from the lighting circuit in the ceiling.

Then run a 4mm earth from the fitting to either the existing bathroom equi-potential bonding or if none exists, do the bathroom bonding as new.

See Wiki for bonding.

Back box needs to be 45mm depth and bathroom works is notifiable under Part P rules.
 
Your need to take L,N and E via 1.0mm or 1.5mm twin and earth from the lighting circuit in the ceiling.

Then run a 4mm earth from the fitting to either the existing bathroom equi-potential bonding or if none exists, do the bathroom bonding as new.

......if the shaver socket or bathroom lighting is installed within zones 1, 2 or 3.
 