what would the situation be if looking to fit the shaver socket inside a basin unit? Basin unit is 800 wide and 350 high.......
 
Sponsored Links
That would be alright - must be BS EN 61558-2-5 nowadays (post is pre-2008) and if it is a new circuit it must be RCD protected

Also there is no zone 3 now. Just 1, 2 and outside zones
 
Sponsored Links
Yup. EFLI is quite right. This was posted in the days of the 16th.

The diagram posted here still stands, but ignore the zone 3 areas, they are outside the zones.

:oops: Sorry, EF, you've mentioned that but I missed it...
 