Shaver socket

Joined
13 Mar 2010
Messages
620
Reaction score
16
Location
London
Country
United Kingdom
Shaver socket installed in a bathroom.
Its in the bathroom cabinet above the sink.
Its slightly in zone 2 by about 50mm.
RCD protected circuit.

Is it something to worry about.
 
Sponsored Links
Is it definitely in zone 2 as in within 600mm of the edge of the bath?

Shaver supply units complying with BSEN61558-2-5 are permitted within zone 2 if they are located where direct spray from showers is unlikely, so I'd say inside a cabinet is fine.
 