Hi,
Whilst showering, I picked up the shower head at one point and got a relatively strong electric shock from it. The hose and head are chrome and are replacements of the original ones (plastic) that had deteriorated, but they have been used for quite a while without issues.
I tested the head against earth and found that there was a considerable voltage (188V). When I isolate the device at the fuse spur there is no voltage at the shower head.
I suspect that the device is damaged and to further substantiate this I tried turning the regulator half-way and then turning on the shower at the fuse-spur and on occassions, the pump would hum and not impart any extra pressure to the output flow.
What is weird is that the chrome hose connects to the shower enclosure through a plastic threaded coupler and the device enclosure is also plastic, so it seems the voltage is being conducted through the water.
I just got a replacement power shower because given its age and the risk, it is not worth servicing.
I have two concerns at this stage:
1. Why didn't the RCD trip when I got a shock? The shower circuit is connected to the main RCD at the consumer unit. I tested the RCD at the consumer unit using the test button and it did trip in this way.
2. Are these power showers so susceptible to electrocuting users on failure? The chrome hose and head do not help, but even so, it seems the water was conducting in the first instance and not the hose.
Thanks,
Andrew
Whilst showering, I picked up the shower head at one point and got a relatively strong electric shock from it. The hose and head are chrome and are replacements of the original ones (plastic) that had deteriorated, but they have been used for quite a while without issues.
I tested the head against earth and found that there was a considerable voltage (188V). When I isolate the device at the fuse spur there is no voltage at the shower head.
I suspect that the device is damaged and to further substantiate this I tried turning the regulator half-way and then turning on the shower at the fuse-spur and on occassions, the pump would hum and not impart any extra pressure to the output flow.
What is weird is that the chrome hose connects to the shower enclosure through a plastic threaded coupler and the device enclosure is also plastic, so it seems the voltage is being conducted through the water.
I just got a replacement power shower because given its age and the risk, it is not worth servicing.
I have two concerns at this stage:
1. Why didn't the RCD trip when I got a shock? The shower circuit is connected to the main RCD at the consumer unit. I tested the RCD at the consumer unit using the test button and it did trip in this way.
2. Are these power showers so susceptible to electrocuting users on failure? The chrome hose and head do not help, but even so, it seems the water was conducting in the first instance and not the hose.
Thanks,
Andrew